Legrand Smarther Thermostat 0 490 39 hysteresis issue for cooling
<p><p>Dear Team!</p><p>I have 4 pcs Smarther with Netatmo Thermostat 0 490 39 integrated in Home + Control with Firmware: 40. This Thermostat can use for heating / cooling. </p><p>I use the thermostats since end of June with a heat pump.</p><p>In the advanced settings can be set the heating algorithm based on the user manual: hysterisis or advanced. In my case I have only the heating algorithm: hysteresis. My big problem, that the setting of the threshold has no influence of the cooling control. The thermostat works only with 0,1 C treshold! This cause too frequent switching on and off the heat pump.</p><p>Was this problem announced from other users? </p><p>Can be changed the algorithm by cooling? </p><p>Is there any plan to solve this issue? </p><p>I seen that other Bticino Smarther X8000-X8000W has separate hysteresis adjustment for cooling.</p><p>Thanks in advance!</p></p>
You must be logged in to reply to this topic.