Connected outlet NLP 78 Firmware
Good morning,
I can’t install zigbee NLP component Firmware update, (power socket) v78 version,
available on your site.
Indeed, when I launch the installation from my own zigbee network with my own gateway, I receive an error code 0x96: ‘invalid image’.
In order to have a clear heart,
I had my power outlet connected to the official Legrand gateway
This one is well updated with v78 visible on the interface.
When I reintegrate it into my own networks, I see this from my updated and reintegrated powersocket :
OTA request ‘{“fieldControl”:0,”manufacturerCode”:4129,”imageType”:17,”fileVersion”:5129215}’
We can notice that the version after the update by your gateway is this one “5129215”
On my other power socket which are not up to date I receive:
OTA request ‘{“fieldControl”:0,”manufacturerCode”:4129,”imageType”:17,”fileVersion”:4867071}’
which corresponds to V74: “4867071”
However with your v78 file available on your site, I detect this
meta version {“fileVersion”:5128707,
I see that the version of the file is not the same as that issued by my power socket after the update via the official gateway
So two concerns for me
The first is that the file available on your site does not seem to be acceptable for the power outlet (NLP) and in addition the version proposed is not the correct one.
Cordially
Hello,
I just uploaded the NLP-81 firmware. I let you check and test
Have a good day,
Leslie – Community Manager
Key : 01:03:05:07:09:0B:0D:0F:00:02:04:06:08:0A:0C:0D
Network address
0x8071
zbee_nwk.addr == 0x8071
Hello Clément,
Here is the feedback from the devs :
We see that the product downloads the firmware starting the offstet 78 and not offstet 0. This case is hard to understand as it’s not reproduced on our side with our gateways and zigbee gateways tested
Can you try the following :
- perform an electrical reboot of the device (and wait at least 30 seconds)
or
- make a factory reset, reinstall the device, then re-try to perform the update
It should help to find the problem
We found the solution and a root cause
Perform an electrical reboot with 30 sec or more, not reset OTA stack of the devices…
so when the devices ask the offset 50 (not 78 have you seen 78 its the starting firmware)
we send more than expected, the devices reset the OTA stack and we can retry update from offset 0
so why the device ask offset 50? its because the software which we uses capping the OTA size response of 50
but Legrand firmware not appreciated that and want the firmware with the size who it ask, the Legrand Firmware still asks for the last bit that it is missing but it does not accept it and falls into a loop.
NLV and NLP product tested !
https://github.com/Koenkk/zigbee-herdsman-converters/pull/6193
After reading the zigbee documentation
https://csa-iot.org/wp-content/uploads/2022/01/07-5123-08-Zigbee-Cluster-Library-1.pdf#page1051
Article
11.13.6.2.6 Maximum Data Size
The value indicates the largest possible length of data (in bytes) that the client can receive at once. The server SHALL respect the value and not send the data that is larger than the maximum data size. The server MAY send the data that is smaller than the maximum data size value, for example, to account for source routing payload overhead if the client is multiple hops away. By having the client send both file offset and maximum data size in every command, it eliminates the burden on the server for having to remember the information for each client.
and articles
11.13.8.2.6 Data Size
The value indicates the length of the image data (in bytes) that is being included in the command. The value
MAY be equal or smaller than the maximum data size value requested by the client. See section 11.11.2 for
more description.
So my conclusion its was your firmware cannot accepte a smaller size wich devices aksing so you dont respect the ZigbeeStack
Hello Clément,
The problem is now clear for the devs and they understand why it wasn’t reproduced on their side
They will fix the max lenght of frame sent by the gateway (but it’s not still prioritized so I don’t know when it will be done)
But the update of your devices will be impossible without a fix on your gateway’s side. We see that the code on gateway was patched last week (GitHub). It seems that you manage to update products. Do you still have problems since this patch was done ?
Have a good day,
Leslie – Community Manager
They will fix the max lenght of frame sent by the gateway (but it’s not still prioritized so I don’t know when it will be done)
The problem is not on your official gateway but with my gateway with Z2M software
But its the devices who need to be fixed to accept a smaler size of OTA block
And yes we can update the product after removing the limitation of my gateway to respond with maximum size of 64 bytes
I expressed myself badly, I meant they will fix the size problem to fit with the zigbee library specs